450.3 (B) ocp in both primary and sec. 480 - 240/120 150KVA
Primary ocp sized at 250% Secondary ocp sized at 125% you have to feed the transformer with the same size wire that is on the secondary side, 450a wire. My application transformer will be right beside the panel feeding it, and right next to that the panel that the transformer is feeding will be mounted, so there is not alot of cost for the wire, but it seems unrealistic to feed with 1 size wire, double the amps thru the xformer then leave the xformer with the same size wire that came in at 1/2 the amps. I do understand inrush current (I think).
How likely is it that the primary ocp would trip if sized at 125% or some number lower than 250?
Is there a rule of thumb that you use?
Primary ocp sized at 250% Secondary ocp sized at 125% you have to feed the transformer with the same size wire that is on the secondary side, 450a wire. My application transformer will be right beside the panel feeding it, and right next to that the panel that the transformer is feeding will be mounted, so there is not alot of cost for the wire, but it seems unrealistic to feed with 1 size wire, double the amps thru the xformer then leave the xformer with the same size wire that came in at 1/2 the amps. I do understand inrush current (I think).