what is an electrical inspectors job?

Status
Not open for further replies.

jbwhite

Senior Member
I was on a job and we were in the process of walking through the building on final inspection. I had done allot of jobs where this same inspector came to check out my work, so he knew how I did things.

As we went down one hall he tried to turn on the lights using one three way. At the other end he tried the other three way. The second switch did not turn off the lights. He didn't say a word and continued his inspection.

When he was done he signed the building permit. I asked if I had to fix the three way before he could sign me off. He said no. He told me that it was his job to insure that the work was safe, and my job to insure that it works.

What do the rest of you think about this inspectors interpretation about the scope of his authority?
 

hurk27

Senior Member
Re: what is an electrical inspectors job?

Your inspector was correct.
And how could he site you as three-ways are not required anyways, As long as one switch operated the light it was code compliant. the other switch was a dummy. :D

Ok I have my umbrella, start throwing. :D
 

ryan_618

Senior Member
Re: what is an electrical inspectors job?

I agree with Wayne, and I agree with your inspector.

I flip every switch in a house, but I don't care if the lights turn on, I only care if the breaker trips.
What do inspectors do?
Well, I drink a LOT of coffee every day :)
 

sandsnow

Senior Member
Re: what is an electrical inspectors job?

I would care if a 3way worked only if required for a stairway.
I would care if a required wall switch controlled light outlet did not work by it's designated switch.
Above applies to residential.
As far as commercial goes, generally you don't need any switching.
All the above applies to NEC only. In CA we have enrgy standards, and working lighting controls is a big deal in our enforcement of these standards. With the more complex controls, the contractor is required to "sign his life away" that they work.

If you hook up an HOA or start-stop to a motor, I would care less if it worked, but only if it had proper SC/GF, OL, and disconnect to pass it.

So yeah, if its safe and functionally meets code, then the rest of the function is your problem; well actually the client.

I drink a lot of coffee in the morning, a lot of diet soda in the afternoon, and not as much beer as I used to in the evening. I had to give up tequila shooters. ;)
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Re: what is an electrical inspectors job?

none of you have even mentioned all the time we spend taking that ill gotten money take to the bank.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: what is an electrical inspectors job?

Originally posted by augie47:
none of you have even mentioned all the time we spend taking that ill gotten money take to the bank.
I was afraid if I did you inspectors would have me silenced by IAEI tough guys. :eek:
 

sandsnow

Senior Member
Re: what is an electrical inspectors job?

Originally posted by augie47:
none of you have even mentioned all the time we spend taking that ill gotten money take to the bank.
I didn't mention it because we are not allowed to take money for bribes. It is shocking that you are allowed to do this. ;)

Actually, I do not solicit gifts to pass violations, however the contractor has to swear that he will never work in out city ever again. ;)
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: what is an electrical inspectors job?

Larry, there is one part of your first post in this thread that is particularly troubling to me,

I had to give up tequila shooters.
why? :( :D

Roger
 

bphgravity

Senior Member
Location
Florida
Re: what is an electrical inspectors job?

I usually make an effort to at least provide an advisory so the contractor/builder is aware and can make the corrections before the home owner catches it or the CO is awarded.

And depending on the particular situation, I will pass violations on the rough if I feel it can be corrected for final inspection. (for things that will still be inspectable) Of course, if the issue has not been corrected by final inspection, the will be cited for the violation.
 

sandsnow

Senior Member
Re: what is an electrical inspectors job?

Originally posted by bphgravity:
I usually make an effort to at least provide an advisory so the contractor/builder is aware and can make the corrections before the home owner catches it or the CO is awarded.

And depending on the particular situation, I will pass violations on the rough if I feel it can be corrected for final inspection. (for things that will still be inspectable) Of course, if the issue has not been corrected by final inspection, the will be cited for the violation.
Bryan, for crying out loud. You could at least keep up the appearance that we're all totally unreasonable and have delusions of our own self importance. I have to say I don't consider you a brother inspector. :( :D ;)

Seriously:
Just like you it depends upon the violation on whether I trust him to correct something by final. Too many other factors in play. Such as the owner or GC not wanting to pay the cost. And the cost is even more in time and money to fix it at final. I don't enjoy holding up the job, I make every effort not to, but I don't enjoy holding up the final even more. I too give advice and warnings early in the job that a certain installation is going to create a problem or the designer has a code violation on the plans.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: what is an electrical inspectors job?

Quick poll: Would no lamps installed in a house violate a code? I've been failed for that in the past, and was curious if it was technically a violation. (The customer provided fixtures and forgot the lamps.)
 

jimwalker

Senior Member
Location
TAMPA FLORIDA
Re: what is an electrical inspectors job?

If it was a luminaire that's required i would say yes.But how does the code actually say this.You have the required outlet.Never been failed for it and customer supplied fixtures never seem to have bulbs.Some will even think you should supply them.Part that upsets me is when they think on the punch out you should now install them.
As to bribes ,what is the going rate ? Will a 20 in the panel be ok ? ;)
 
Re: what is an electrical inspectors job?

As an inspector in Canada, I can only comment on what I, and what I would expect other Canadian inspectors, would do in this case.

I would bounce this as a dificency. Yes... we have a responsibility to find the "un-safe" installs, but we also have a responsilibilty to ensure things work as intended.

Wether or not the installed systems meet the customers need is not in our area of concern. What is in our area, or should be IMHO, is that what is installed works as it should.

The Canadian code has clear rules about "Quality of Workmanship" and that "Electrical Systems" are maintained in working order. This issue, of the faulty three way switching, clearly "meets" the intent of those rules and as such should be bounced by most inspectors in Canada, and I hope by those in America as well.

[ January 06, 2006, 10:07 AM: Message edited by: Rick Kelly ]
 

earlydean

Senior Member
Re: what is an electrical inspectors job?

actually the NEC does not require any luminaires, only lighting outlets. The building code requires illumination in stairwells, and illumination of the egress, but daylight could provide those as well. To turn down a CO for lack of lamps is silly.
 

Cavie

Senior Member
Location
SW Florida
I agree. To turn down would be silly but with enough of these and other turndowns, the Quaility of workman ship would improve greatly. It's not beeing "Hard nosed", it's about being a teacher. The workmanship in our trade has gone out the window. let's try to get it back.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Cavie, how is my workmanship in question if the fixture is installed correctly and the customer neglected to provide me with bulbs, and then neglected to get them installed before inspection?
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
I always get the agument that they need their power released for final inspection, otherwise how could I tell if it works. I do a final to see if you should get power.

I say the same thing your inspector did. My jobs to insure you install it per the NEC, your job is to make sure it works.

No where in the NEC does it say the light has to come on when you flip the switch.

I once installed a fan/light for a woman. I had the breaker off since I had to cut into some lines and hadn't turned it back on yet, anyways she comes in the room just as I'm starting to clean up and flips the switch and nothing happens. She says "it doesn't work". I said "no ma'am how could it they're not wired together". "What?". I said "read my contract, it says install one ceiling fan and one wall switch. I doesn't say anything about wire, if you want it to work that's gonna be an extra."

Luckly she had a good sense of humor.
 

dnem

Senior Member
Location
Ohio
ryan_618 said:
I agree with Wayne, and I agree with your inspector.

I flip every switch in a house, but I don't care if the lights turn on, I only care if the breaker trips.
sandsnow said:
I would care if a 3way worked only if required for a stairway.
I would care if a required wall switch controlled light outlet did not work by it's designated switch.
Above applies to residential.
As far as commercial goes, generally you don't need any switching.
I agree but would add one more category of light that needs to work on the final. In both residential and commercial egrees lighting must work.
cowboyjwc said:
I always get the agument that they need their power released for final inspection, otherwise how could I tell if it works. I do a final to see if you should get power.
We require separate service main and final inspections because we require power to do the final.

There would be two problems that would come from not having power on a final.
1) You can't check lighting in stairways or egree lighting.
You can't check switched plugs or proper termination of all plugs thruout the building [particularly attachment of equipment grounding] without demoing all of the plugs.
2) One of our power companies that serves one area of the county might take anywhere from 3 days to 6 weeks to hook up the service. If you add this on the end of the completed building, all contractor schedules would go to hell and customers wouldn't know when they could move in.

David
 