Here is a document my building department recently posted regarding this issue:
Re: Changes to Building Department Requirements for Final Electrical Inspection
To Whom It May Concern:
Effective March 1st 2006, all buildings and structures will be required to have electrical utilities connected before Final Electrical Inspection. The following reasons are listed for this change:
1. To verify completed wiring is free from short circuits and from grounds other than as required or permitted in Article 250 per Section 110.7 of the 2002 NEC.
2. To verify the panelboard circuit directory correctly identifies the purpose or use of all branch circuit breakers per Section 408.4 of the 2002 NEC.
3. To verify ground-fault and arc-fault circuit protection of devices and outlets where required by the code per Section 210.8 and 210.12 of the 2002 NEC.
4. To verify proper operation of all required egress lighting per Section 210.70 of the 2002 NEC and Section 1006 of the 2004 Florida Building Code.
Please contact the Building Department if you have any questions on this matter.