what is class2
websparky
Cleveland, Ohio
Re: what is class2
The quick unofficial answer;
A circuit that originates from a non-autotransformer and usually has a voltage less than 50V.
Yes, the cables can be run in conduit.
[ November 06, 2003, 10:45 PM: Message edited by: websparky ]
don_resqcapt19
Illinois
retired electrician
Re: what is class2
Class 2 Circuit. The portion of the wiring system between the load side of a Class 2 power source and the connected equipment. Due to its power limitations, a Class 2 circuit considers safety from a fire initiation standpoint and provides acceptable protection from electric shock.
The only time you can have a Class 2 circuit is when the power source for the circuit origniates from a listed Class 2 power supply. Class 2 circuits can be in conduit, but not along with power or Class 1 circuits.
Don
[ November 06, 2003, 09:29 PM: Message edited by: don_resqcapt19 ]