What is meant by "Explosion Protected"?

Status
Not open for further replies.

KentAT

Senior Member
Location
Northeastern PA
So Allen-Bradley uses the terms "Explosion-Protected" to describe their 800TC- switch contact blocks. I have never seen this term used before. Is this a marketing thing or does "explosion-protected" have meaning in the NEC or UL?
 

Attachments

  • 800TC.JPG
    800TC.JPG
    110.4 KB · Views: 0
Last edited:

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
they can call it anything they want to. it is listed for use in C!D2 areas. That is the important thing.
From what I can tell it isn't listed for anything. I tried researching it at UL's Certification site which UL has now transmogrified to virtually useless. In any case, I learned to ask manufactures for the UL "E- number" unless the ad material actually indicates a certification mark.

This does not mean the product is unsuitable for Division 2, simply more due-diligence is necessary.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Last edited: