Help me out here. I am looking at the 2011 NEC Draft, and confused by the following:
What does this section mean?
Having nowhere else to turn, I've googled "nonsinusoidal" and realized that it is refering to a sine wave that has been altered in such a way as to be "un-sine-wavy". What normal processes are used to achieve this result intentionally in a pool setting?
Does a Class 2 transformer alter a sine wave?
Thanks in advance,
Now, I am just a dumb electrician, so I would appreciate if the responses are tailored in such a way that I can understand.680.13 Voltages for Wet Contact. Requirements of this article recognized for an operating voltage of 15 volts or less and for an operating voltage of more than 15 volts are based the assumed use of sinusoidal ac. Where the supply source is other than sinusoidal ac, the following wet contact voltage values shall apply instead of 15 volts sinusoidal ac:
(1) 21.2 volts peak for nonsinusoidal ac.
(2) 30 volts for continuous dc.
(3) 12.4 volts peak for dc that is interrupted at a rate of 10
to 200 Hz.
What does this section mean?
Having nowhere else to turn, I've googled "nonsinusoidal" and realized that it is refering to a sine wave that has been altered in such a way as to be "un-sine-wavy". What normal processes are used to achieve this result intentionally in a pool setting?
Does a Class 2 transformer alter a sine wave?