I just returned from a service call for a customer that was blowing a 200A fuse on new feeder conductors. I meggered all the wires and there is no insulation resistance problem, so I turned on the disconnect and all is well. I believe it was user error in the first place, but that?s not the problem now.
Now here?s something I?ve never seen before. With the feeder conductors installed in the underground RMC and not landed on any terminals at neither the source nor the branch panel; I read 277V on my DMM between any phase at the source and any of the conductors. What is going on? I spoke with an engineer and a senior electrician and they both referenced ?Phantom Voltage?, but with no explanation.
The feeder conductors are fed out of an 800A 480/277V Switchboard. The grounding and bonding appear to be appropriate, but I did not perform a ground-resistance check.
I?m looking forward to hearing about this.
Now here?s something I?ve never seen before. With the feeder conductors installed in the underground RMC and not landed on any terminals at neither the source nor the branch panel; I read 277V on my DMM between any phase at the source and any of the conductors. What is going on? I spoke with an engineer and a senior electrician and they both referenced ?Phantom Voltage?, but with no explanation.
The feeder conductors are fed out of an 800A 480/277V Switchboard. The grounding and bonding appear to be appropriate, but I did not perform a ground-resistance check.
I?m looking forward to hearing about this.