Every electrician I ask tell me different story
This is important since wire are very expensive
I am need to connect an air-condition rated 240 50 Amp 3 wires (2 hot and ground)
According to the NEC
Table 310.16 Allowable Ampacities of Insulated Conductors Rated 0 Through 2000 Volts, 60?C Through 90?C (140?F Through 194?F), Not More Than Three Current-Carrying Conductors in Raceway, Cable, or Earth (Directly Buried), Based on Ambient Temperature of 30?C (86?F)
Types RHW, THHW, THW, THWN, XHHW, USE, ZW
For 60?C (140?F) is 40 amp
And for 75?C (167?F) is 50 amp
What is this temperature? Is it the temperature in the attic where I put the wire?
Also from the NEC 2002 book
8 AWG THHN, 90?C copper wire is limited to 40 amperes where connected to a disconnect switch with terminals rated at 60?C. This same 8 AWG THHN, 90?C wire is limited to 50 Amp
Can someone tell me if I can use 8 AWG THHN
Moderators note: Personal contact information removed, please use PM to exchange this info
Thank you
This is important since wire are very expensive
I am need to connect an air-condition rated 240 50 Amp 3 wires (2 hot and ground)
According to the NEC
Table 310.16 Allowable Ampacities of Insulated Conductors Rated 0 Through 2000 Volts, 60?C Through 90?C (140?F Through 194?F), Not More Than Three Current-Carrying Conductors in Raceway, Cable, or Earth (Directly Buried), Based on Ambient Temperature of 30?C (86?F)
Types RHW, THHW, THW, THWN, XHHW, USE, ZW
For 60?C (140?F) is 40 amp
And for 75?C (167?F) is 50 amp
What is this temperature? Is it the temperature in the attic where I put the wire?
Also from the NEC 2002 book
8 AWG THHN, 90?C copper wire is limited to 40 amperes where connected to a disconnect switch with terminals rated at 60?C. This same 8 AWG THHN, 90?C wire is limited to 50 Amp
Can someone tell me if I can use 8 AWG THHN
Moderators note: Personal contact information removed, please use PM to exchange this info
Thank you