what is the answer to these questions?

For #1 - we use #6 since next size up 65 amps would be 70amps which would equal 70 amps

For #2 - we choose #6 because if we choose #8, next size up would be 45 amps and not 50 amps on table 240.(6)A

And for #3 - we choose # 8 and not #10 as next size up for #10 would be 40 amps and not 50 amps.
1) is correct
2) is correct
3) #8=50 amps there is no next size up so #8 is the answer.
 
I get it guys.. thank you.

It's basically next size up rule.
So,
For #1 - we use #6 since next size up 65 amps would be 70amps which would equal 70 amps

For #2 - we choose #6 because if we choose #8, next size up would be 45 amps and not 50 amps on table 240.(6)A

And for #3 - we choose # 8 and not #10 as next size up for #10 would be 40 amps and not 50 amps.

Is my logic now correct? or no? please let me know.. ty
Right answers but logic on #2 and #3 is a bit off.
Since 40A is the 75C ampacity of 8awg and 40A is also a standard breaker you don't get to use the next size up no matter what that size might be. Similarly for the #10, with the additional detail that 240.4(B) generally does not allow the next size up rule for 10awg and smaller.
 
with the additional detail that 240.4(B) generally does not allow the next size up rule for 10awg and smaller.
I think you meant 240.4(D)?

There's no special interaction between 240.4(B) and 240.4(D), since the standard ampacities of #10, #12, and #14, at both 60C and 75C, are standard breaker sizes. And 240.4(B) can certainly be used when there is significant derating. E.g. (10) 14/2 NM cable crammed together in a hole through a framing member which is insulated. Very likely that's 20 CCC, so 0.5 ampacity adjustment, so an ampacity of 12.5A. Still fine to protect at 15A if they are supplying circuits other than multiple receptacles and with a calculated load of 12.5A or less.

But if any of the test questions were asking about 15A-30A breakers, then 240.4(D) would be something you need to follow.

Cheers, Wayne
 
I think thst you meant #8 @ 75° C has an ampacity of 50 amps not 40.
That was regarding question #2 in the OP which said to use 60C

I think you meant 240.4(D)?
Yes. Sorry, that was a confusing typo.

There's no special interaction between 240.4(B) and 240.4(D), since the standard ampacities of #10, #12, and #14, at both 60C and 75C, are standard breaker sizes. And 240.4(B) can certainly be used when there is significant derating. E.g. (10) 14/2 NM cable crammed together in a hole through a framing member which is insulated. Very likely that's 20 CCC, so 0.5 ampacity adjustment, so an ampacity of 12.5A. Still fine to protect at 15A if they are supplying circuits other than multiple receptacles and with a calculated load of 12.5A or less.

But if any of the test questions were asking about 15A-30A breakers, then 240.4(D) would be something you need to follow.

Yes agree, but my point was we can simply state that if you're thinking of using 10awg copper (and not 240.4(G) and taps don't apply) on a 40A breaker you just stop, because you can't.
 
@solar man The next size up rule is used only when the load is not over the conductor ampacity. Since none of the questions gives a calculated load then I would go straight from the table.

Eample of next size up. Say you use a #6 NM cable that is rated at 60C. The max the conductor is allowed is 55 amps. Since 55 amps is not a standard size breaker you can use a 60 amp breaker only if the calculated load isn't greater than 55 amps. Does that help
 
@solar man The next size up rule is used only when the load is not over the conductor ampacity. Since none of the questions gives a calculated load then I would go straight from the table.

Eample of next size up. Say you use a #6 NM cable that is rated at 60C. The max the conductor is allowed is 55 amps. Since 55 amps is not a standard size breaker you can use a 60 amp breaker only if the calculated load isn't greater than 55 amps. Does that help

Yeah I understand that it applies to next size up of the OCPD - this is I guess reverse next size up condition...
 