Coppersmith
Senior Member
- Location
- Tampa, FL, USA
- Occupation
- Electrical Contractor
I've been hired to do a panel change. The existing panel is behind the washer and the washer cannot move. All of the branch wiring enters the panel at the top. Since this is a working space violation and there isn't another good spot for the panel inside, I plan on installing the new panel outside on the opposite side of the wall from the existing panel (next to the meter).
The issue I have is how to reasonable connect the branch wiring. If I leave the existing cabinet as a junction box I can bring conduit out the bottom, penetrate the wall and pipe into the bottom of the new panel. I've got 38 CCC's plus I need some reserve. This would require a bunch of conduits (probably 6 x 3/4") to avoid derating below 70% per 310.15(B)(3)(A). The MWBC trick doesn't help here since it all existing wiring.
I'm wondering if it would be code compliant to connect the branch together with individual UF cables. If they exit both the new panel and the old from the bottom, I could run them through a row of small penetrations and then cover them with a sheet metal cover for physical protection and also secure them to the wall. Thoughts?
Am I allowed to use standard (non-weatherproof) NM connectors outside if on the bottom and covered?
The issue I have is how to reasonable connect the branch wiring. If I leave the existing cabinet as a junction box I can bring conduit out the bottom, penetrate the wall and pipe into the bottom of the new panel. I've got 38 CCC's plus I need some reserve. This would require a bunch of conduits (probably 6 x 3/4") to avoid derating below 70% per 310.15(B)(3)(A). The MWBC trick doesn't help here since it all existing wiring.
I'm wondering if it would be code compliant to connect the branch together with individual UF cables. If they exit both the new panel and the old from the bottom, I could run them through a row of small penetrations and then cover them with a sheet metal cover for physical protection and also secure them to the wall. Thoughts?
Am I allowed to use standard (non-weatherproof) NM connectors outside if on the bottom and covered?