I would like to know the code requirements for installing High Bay Flourescent lighting. Can you run cord? How far? Does it have to have a plug or can it be hard wired?
I would like to know the code requirements for installing High Bay Fluorescent lighting. Can you run cord? How far? Does it have to have a plug or can it be hard wired?
We done quite a few HID to Fluorescent conversions. While the energy savings is there, it becomes a maintenance headache. You now have 4 or 6 times the amount of lamps to maintain.
We done quite a few HID to Flourescent conversions. While the energy savings is there, it becomes a maintenance headache. You now have 4 or 6 times the amount of lamps to maintain.
Most highbay fluorescent lighting can be ordered with a 6' twist lock cord and plug so if the original install was twist loc then the swap out is easy, I favor the T-5 lamp with mirror reflector fixture as the lumen's per watt is higher then the T-8 and the light output is much higher, also using a twist loc cord and plug is nice when it comes time to replace a ballast or somthing as you just unplug it and take the fixture down (put it on hooks) and do the work on a bench at ground level.
How so?
Most quality T-5 highbay fixtures come with parallel ballast which means if one lamp goes out the rest stay lit, I have found this as well as my customers as a good advantage as a much larger area just doesn't go dark like if you loose a 400 watt HID lamp, matter of fact most don't even notice that a lamp went out, with good T-5's pushing 40k hours it doesn't happen that often either, there are also other advantages to these as they are instant on which as was pointed out motion sensor, 3-ways switching makes sense, short term power failures are not a problem anymore, this on top of the wattage savings makes for a pretty good sale.
I tend to be fond of the RUUD ones while they are a little pricy they stand behind them, and I have very little trouble with installs using them, also they sell direct which means lower cost then going through a middle man, to get prices you have to sign up to there web site though.
Most highbay fluorescent lighting can be ordered with a 6' twist lock cord and plug so if the original install was twist loc then the swap out is easy, I favor the T-5 lamp with mirror reflector fixture as the lumen's per watt is higher then the T-8 and the light output is much higher, also using a twist loc cord and plug is nice when it comes time to replace a ballast or somthing as you just unplug it and take the fixture down (put it on hooks) and do the work on a bench at ground level.
Where are you seeing that T-5's have more lumens per watt? It is most likely true in a high-bay application where the fixtures stay warmer (which makes T-5's slightly more efficient).
You have to keep in mind that the ballasts are also part of the load equation. When you take into account the load of the system (ballast and lamp), in general T-8's outperform T-5's in the lumens per watt category(based on available published system lumens and watts from a lamp/ballast cut sheet or catalog). If you are seeing info to the contrary, I'd like to see it.
For instance, using the GE 2010 lamp and ballast catalog:
F32T8/SP30/ECO lamps are rated for 2660 mean lumens. Ultrastart PS 2-lamp T8 ballast uses 59 watts with a 1.14 ballast factor. Lumens/watt = 2x2660x1.14/59 = 102 L/W.
F28T5/830/ECO lamps are rated for 2660 mean lumens. Ultrastart PS 2-lamp T5 ballast uses 70 watts with a 1.16 ballast factor. Lumens/watt = 2x2660x1.16/70 = 88 L/W.
F54T5/830/ECO lamps are rated for 4600 mean lumens. Ultrastart HO PS 2-lamp T5HO ballast uses 114 watts with a 1.00 ballast factor. Lumens/watt = 2x4600x1.00/114 = 81 L/W.
These are specific examples, and there are many variables that can be changed, but this example is very typical.
I visit this discussion often with other colleagues in the lighting industry, and I still don't see many uses where the T5 outperforms the T8, especially when you factor in the cost of the lamps. The big exception being high bay applications where you simply can't live without the vast number of total lumens that the T5HO provides, and efficency is less of a concern.
I guess I should have read a little more on T8's then I have,I still don't know why ballast manufactures have this much less wattage rating on 2 32 watt lamps when including the ballast then any other type of lamp, in most all cases except a T-8 a two lamp ballast will always show a rating that will include the wattage of the two lamps and a small ballast wattage resulting in a rating that is a few watts above the total lamp wattage, such as the rating of T-5 at 117 watts for a two lamp ballast and two 54 watt lamps.
But after looking at the specs of a couple ballast manufactures they all state a 59 watt input rating for a two 32 watt T-8 lamp ballast???? Now I am confused, if a 32 watt T-8 lamp has a 32 watt rating which is 64 watts for two, how is it that the ballast will only use 59 watts?
I would like to know the code requirements for installing High Bay Flourescent lighting. Can you run cord? How far? Does it have to have a plug or can it be hard wired?