What is the Minimum breaker size required by NEC for #14 Copper wire feeding a A/C minimum 18.5 amp and 25 amp Max over current protection?

Status
Not open for further replies.

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

What size wire, of the type (NM, MC, THWN, etc.) you intend to use is rated at 18.5a or better?

We usually don't like to just answer such questions, preferring to teach you how to figure it out.

Added: Is that 18.5a the MCA or minimum breaker?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Do you mean a MCA of 18.5 and a max OCPD of 25 as stated on the label? If so the conductors could be #14 using 75 degree conductors (pipe and wire) of if using NM cable they would need to be #12 as NM must use the 60 degree ampacity.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
NM cable is limited to the 60° C ampacity which is 15 amps for #14 AWG. Use MC cable or pipe and wire and you can use the 75° C ampacity.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Doesn’t #14 Copper have an asterisk and footnote requiring 15 amp breaker maximum and #12 20 amp breaker Maximum and #10 30 amp max?
The * in the ampacity table sends you to 240.4(D), the small conductor rule. The parent text says the rules in 240.4(E) or (G) can override the small conductor rule. The rule in 240.4(G) says that the conductor sizing and overcurrent protection rules in Article 440 apply to air conditioning circuits.
 
Location
2974 Copperopolis, Ca
Occupation
Electrical Contractor since 1978
Yes 14-2 romex
The * in the ampacity table sends you to 240.4(D), the small conductor rule. The parent text says the rules in 240.4(E) or (G) can override the small conductor rule. The rule in 240.4(G) says that the conductor sizing and overcurrent protection rules in Article 440 apply to air conditioning circuits.
So 14-2 Romex is allowed on a 20 amp breaker?
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
Yes, if it feeds a motor, HVAC unit, or some of the other exceptions. The MCA would need to be 15A or less though.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The title and the first post are different questions.
What is the minimum wire size required by NEC for a A/C mini split system with a minimum 18.5 amp and Maximum 25 amp over current protection?

If this is the question then I would say 14 gauge wire is fine with a 25 amp overcurrent protective device. That is assuming it is not nm cable. Since the info isn't given then I would use t. 310.16
 