What is the perimeter of Class 1 div 1 area, NEC section B.1.2

Status
Not open for further replies.

fandi

Senior Member
Location
Los Angeles
Hello all,
I'm installing disc. sw and vfd for a new cooling tower in an outdoor location. There's a big long white propane tank 5 ft away (still outdoors). A chain fence separate the tank and the cooling tower+elec equipment. It seems to me that flammable gas may exist because of leakage. Can I install the elec equipment behind the cooling tower so that they're hidden from the tank and therefore the elec equipment doesn't have to be classified?
Thanks a lot.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Please review your reference; I have no idea what "NEC section B.1.2" is.

That said, depending on the processes involved, cooling towers themselves are often considered sources.
 

fandi

Senior Member
Location
Los Angeles
Please review your reference; I have no idea what "NEC section B.1.2" is.

That said, depending on the processes involved, cooling towers themselves are often considered sources.
Sorry, it's Art. 500.5.B.1.2 aka definition of Class I Div. 1. but I thought Cooling Towers are not considered hazardous locations other than the electrical equipment shall be in Nema 4X enclosures?
Thanks, Bob.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
As I mentioned, it depends on the processes involved. A cooling tower serving shell and tube heat exchangers often receive flammable products that have leaked from the process tubes. See API RP500 Section 9.2.4 / Figure 28 for example.

You really need someone that is familiar with the whole process design to determine a proper electrical classification document. [Section 500.4(A)]
 