mshields
- Boston, MA
On a 480V service rated say 600A, the NEC would not require ground fault. But would ground fault provide added protection of the system? What is the rational behind setting the requirement at 1000A?
But the requirement for GFP on services 1000A and over applies to fuses too....In the days before the GF trip requirement, I had my own guess or assumption that over 600 Amp, the breaker could see the arc like a normal load and just stay on. Fuses I would trust to open, but not the old breakers. Seen and heard of enough stories of stuff that just kept burning.
...It serves only to limit damage to conductors and equipment
on the load side in the event of an arcing ground fault on
the load side of the protective element.
I wouldn't be surprised if it wasn't the result of a negotiation.
1st guy: All services @any size.
2nd guy: 480V @4000A+
..... 2 weeks later
ok ... more than 150 to ground up to 1000 Phase to Phase and 1000A+
rated 1000 amperes or more and installed on solidly grounded wye electrical systems of more than 150 volts to ground, but not exceeding 600 volts phase-to-phase,