What is voltage imbalance. Is it one phase has more voltage then the other?

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
Reading some notes I took from a class a few years ago. It says 1% or over must be eleminated. Thanks for your help.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
100124-1827 EST

Why pick on 1%? Suppose I have a 120-0-120 supply and one single phase load of 200 A, a real big heater, can not split it. I am likely to have 5% or more difference, maybe 10% because the power company does not put in a very large transformer.

.
 

mivey

Senior Member
For poly phase systems:
% unbalance = 100 * maximum deviation from average voltage / average voltage.

According to ANSI C84.1:
Supply systems should be at 3% or less at the meter under no-load conditions. 98% of systems surveyed are within 3% and 66% of the systems surveyed were with 1% unbalance.

That said, when you get to the 0.5-1% range, you might expect to have to derate the equipment. Your class notes were probably referring to what you need to do to avoid derating the equipment.

Add: In the formula, use line-line voltages.
 

quogueelectric

Senior Member
Location
new york
Reading some notes I took from a class a few years ago. It says 1% or over must be eleminated. Thanks for your help.
For example if a service would be delivered on the fringe edge of pocos distribution they may have 600 homes tapped off the primary phase A 200 homes tapped off the primary phase B and 1000 homes tapped off the primary phase C. This because of poorly distributed load can cause a substantial voltage difference on the voltages measured to ground on A,B,and C phase .
 