What is wrong here

Status
Not open for further replies.
Why? Is the HVAC three phase? What else would use the high leg? Why not transform it down to 208 so that the load can be balanced?

Caveat: I am an engineer, not an electrician. Be gentle with me. :D
We don't have place for pad mounted, utility xfrmrrer
delta -4w it is
only 3-ph elevator, load
voltage supplies from the city is 4wire, delta overhead
 
We don't have place for pad mounted, utility xfrmrrer
...
voltage supplies from the city is 4wire, delta overhead
No place for pad mount has nothing to do with it. I do realize consumers are stuck with whatever the utility says they will make available, but seems strange they will not supply 208/120V 3? 4W.

Never heard of 4-wire delta transmission lines... only 3-wire. 4-wire is always wye, to my knowledge.
 
Perhaps service transformers are open delta with large lighter, small stinger. 3? balancing would actually create a problem.

Service conductor sizes for neutral and high leg could possibly be reduced to match maximum unbalanced load for neutral and load/OCPD-rating for high leg.
We ran into that situation designing and installing a PV system in San Antonio. We ignored the high leg and built it as a 3W 240V split phase interconnect.
 
No place for pad mount has nothing to do with it. I do realize consumers are stuck with whatever the utility says they will make available, but seems strange they will not supply 208/120V 3? 4W.

Never heard of 4-wire delta transmission lines... only 3-wire. 4-wire is always wye, to my knowledge.
Nots that he said supply, not primary.
The service wiring from two or three pole mounted pots is four wire high leg.
 
No place for pad mount has nothing to do with it. I do realize consumers are stuck with whatever the utility says they will make available, but seems strange they will not supply 208/120V 3? 4W.

Never heard of 4-wire delta transmission lines... only 3-wire. 4-wire is always wye, to my knowledge.

The transmission line might be two phase legs only. Then the poco can give you 3-phase with an open-wye, open-delta arrangement of 2 transformers. One clue would be when you see the service coming off of two different size transformers on a pole. I don't think you can get a grounded wye secondary in this case.
 
Nots that he said supply, not primary.
The service wiring from two or three pole mounted pots is four wire high leg.

The transmission line might be two phase legs only. Then the poco can give you 3-phase with an open-wye, open-delta arrangement of 2 transformers. One clue would be when you see the service coming off of two different size transformers on a pole. I don't think you can get a grounded wye secondary in this case.
Both good points and likely they be... ;)
 
Yeah, but they usually keep track of several such open deltas on their primary and rotate the phases to balance their primary.
As well as all the single phase services they supply need to be balanced across the primary lines - for their benefit.
 