Gus,
I was wondering that myself...I looked at the square D website for transformer connections. It appears that terminals X2 and X3 are being connected (as it center tap) which would require bonding it to ground to comply with NEC.
Instead X1 and X4 are utilized to derive 240V and either X1-X2 or X3-X4 for the 120V.
Could you explain what you mena by having both voltages, the primary protection not protecting the secondary?
Thank you.
What I see:
a) Inadequate protection of the step up transformer and its secondary feeders.
b) Tapping of single phase transformer not only does it not comply with the tap rule but also is to take place within the disconnect. Even it it were allowed, depending of where the tap is connected it could be considered a feeder or a branch circuit tap.
c) Single phase transformer lacks proper protection. Since the control enclosure does not have overcurrent protection within it, the primary side protection cannot exceed 125% of FLA.
I suggested relocating the disconnect switch to the secondary side of the step-up transformer and revising the fuse size to 45A (standard size) as per table 450.3(B).
I also recommended providing a junction/splice box for tapping of secondary feeder and and adjacent fused disconnect 2P, 30AS, 20AF to protect the step-down transformer.
Perhaps... but is it necessary? 125% is only 4 more primary amps... so what two more amps at best on the secondary. You might be able to get more inrush capability, but then you'd have to add secondary ocpd and upsize primary ocp. Without knowing the loads, it's kind of hard to do anything but speculateGeneral comment was that the overcurrent protection sizes should be compared against table 450.3(B). The primary protection of the step-up transformer is 120% of the full primary current, thus the transformer cannot be utilized to full capacity.
The fusing is unnecessary.
Smart,
I cannot find article 240.30(C)(1) on the 2005 NEC.
I concur that the transformer should be a 208V delta to 480V wye grounded step-up transformer in lieu of what is indicated. It appears that a standard 480V delta to 120/208 wye was selected and reversed, doesn't it? Are you refering to the ground loops?
Ooops! ...would you believe I made a typo?
Should have been 240.21(C)(1)
It's the same one that requires secondary tap conductor protection for the multi-voltage step down transformer... but in the case of the step up transformer, it appears to be a 3-wire delta, single-voltage secondary. Note part of the criteria is the xfmr be delta-delta connected. Even though its primary windings are wye configured, the connections will be delta-delta.
Yes, it appears to be a delta-wye step-down wired in reverse. No, I'm not referring to ground loops. There is no indication any of the three line conductors will be a grounded conductor. The 3P disconnect suggests none are grounded as you would only need a 2P disconnect if one leg were grounded. If none are grounded, 250.21 would require ground detectors for the secondary.
Distance and raceway type have little bearing on the transformer's secondary and tap conductor protection. If protection of such meets the specifications of 240.21(C)(1), there is no need to complicate by qualifying the tap conductors under another subparagraph, such as 240.21(C)(4). The main paragraph of 240.21(C) is not very explicit in this regard... but if you think about it, there would be no way for every installation to qualify under all six subparagraph. Logic precludes only one needs to be satisfied.The lenght of the secondary feeders between the set-up transformer and the gate controller and access control is approx. 1600' and being in a duct bank (new, resolution to previous post), 240.21(C)(4) applies. Per 240.21(C)(4)(2) allows tapping of the load side of the disconnect to energize any number of additional overcurrent devices. As such, proper primary and secondary protection can be provided for the single phase transformer.
Definitely a concern that needs resolved!!!It still does not correct the lack of grounding on the secondary side of the step-up transformer.
...Logic precludes only one needs to be satisfied.