charlie said:Has that changed? The information I have is:
LV = Voltage levels that are less than or equal to 1 kV
MV = Voltage levels that are greater than 1 kV, but less than or equal to 69 kV
HV = Voltage levels that are greater than 69 kV, but less than or equal to 230 kV
EHV = Voltage levels that are greater than 230 kV, but less than or equal to 800 kV
UHV = Voltage levels that are greater than 800 kV
I agree that this is probably medium voltage cable. I would guess that it is #2 Al. 15 kV GRD Y XLPE (it has a translucent look to it) with either a full or 1/3 size concentric neutral and a PE jacket.![]()
sb1975 said:Thanks everyone, yea I knew it was a high-voltage cable but was unsure what the outer conductors were used for.
Like what we do, the neutral should parallel the line conductor. Remember, a transformer primary needs two conductors, too.Ken 6789 said:Why does the primary cable have a neutral? I thought the neutral is always picked up on the xfmr this cable feeds.
We also use the neutral for grounding. We don't depend on just the ground rod (sound familiar to anyone?) for grounding equipment.LarryFine said:Like what we do, the neutral should parallel the line conductor. Remember, a transformer primary needs two conductors, too.
It works very well when the guy on the backhoe is trying to dig through the cable. The cable will also pull the elbows off if he is close to deadfront equipment.dbuckley said:Just a note about concentric cable; it is used when the neutral conductor is a combined neutral and ground conductor to try and prevent a shock hazard. The logic is that you cant disconnect the neutral through cable damage or failure and still have the hot connected.