pharouff
- Washington, DC
Most of the time our responsibility ends 5 feet from the perimeter of the building; and beyond that point is the commercial utility's responsibility where the NEC does not apply. A utility power cable is considered a "service lateral" until it reaches the first overcurrent protection device where it becomes "premises wiring".
But sometimes we have to deal with a campus power distribution system, where some NEC requirements may apply to the incoming power service. For example, there are requirements in Articles 695.3 and 695.5 which appear to apply to campus-style complexes. Also, there are some who argue that the NEC applies anywhere past the utility meter: the entire campus.
Are power cables from campus substations to individual structures considered "premises wiring" or "service laterals"? Are they sized and installed per the NEC?
Do we need to size exterior campus utility substation transformers per the "NEC" peak demand load or per the "corporate experience" peak demand load similar to a typical utility company?
What if the campus has primary power generation facilities?