Back on topic, what does everyone think of a wire-mold strip under the counter edge?
e57 said:Funny because the above wording is very like what he was using to justify "C" to "D" because the vanity is a counter.... And yes I had both the '99 that the job permit is under, and the '05 CEC open next to each other in the side door of my van - me saying separate - he saying together.
But like I said, he arrived to the job pre-tweeked by a silly Architect trying to go over my head attempting to get something approved that is clearly outside the code. Placing the outlet in cabinets and drawers.... So he wasn't having any of what I was telling him.
e57 said:Back on topic, what does everyone think of a wire-mold strip under the counter edge?
What about a bath vanity?acrwc10 said:on an island I like it.
e57 said:Back on topic, what does everyone think of a wire-mold strip under the counter edge?
Sorry, but I do not agree. That is simply because the function of the OCPD has nothing to do with protecting the outlet/receptacle/receptacle outlet/point on the system/whatever you want to call it. The breaker has only one function, and that is to protect the conductor.wbalsam1 said:I'm only trying (very hard at this point) to maintain the idea that if a branch circuit is assigned a maximum ocpd of 20 amperes, a point on this circuit where current is taken is not protected at 15, but rather 20 amps. Do you agree?
charlie b said:
The breaker has only one function, and that is to protect the conductor.
What is a "wall" receptacle? IMO wiremold mounted on a wall are "wall" mounted receptacles. And since the code elaborates to expand to "partition" that could easily be the face of cabinetry below and adjacent to the basin. Depending on if mounted facing out or down it would also add the safety of a drip loop, if mounted facing down.... :grin: :grin: :grin:stickboy1375 said:The required receptacle shall be at least one WALL receptacle with 3' of the basin. The receptacle shall be located on a wall or partition that is adjacent to the basin or basin counter top.
e57 said:What is a "wall" receptacle? IMO wiremold mounted on a wall are "wall" mounted receptacles. And since the code elaborates to expand to "partition" that could easily be the face of cabinetry below and adjacent to the basin. Depending on if mounted facing out or down it would also add the safety of a drip loop, if mounted facing down.... :grin: :grin: :grin:
charlie b said:Sorry, but I do not agree. That is simply because the function of the OCPD has nothing to do with protecting the outlet/receptacle/receptacle outlet/point on the system/whatever you want to call it. The breaker has only one function, and that is to protect the conductor.
As you can see it is already hard enough....stickboy1375 said:Dont make this harder than it has to be.![]()