Is this a branch circuit or service conductors?
I turn my back on my opinions all the time
What input do you need?
There was no poll at the top when I first responded.
Poll Status to Date.
Those who have answered correctly :smile: --------- 33%
Those who have answered incorrectly :roll:-------- 60%
Those who are wayyyyy off------------------ 6%
Be loyal to truth and a reference, not an opinion.....I turn my back on my opinions all the time
The above results are base on your opinion, not necessarily the opinion of all.
It all depends on how to read 250.122(A) & (F), which without a ruling from the NFPA cannot be decided by a handful of people here on the site.
(have you read 250.122(G) - which is a good example of how EGC can be sized accordingly with the ungrounded conductor. And....feeder tap conductor sizing in ratio can be much smaller in size relative to the overcurrent device size)
Short of a Formal Interpretation or a statement from a code making panel published in the ROP or ROC, I don't see how you can say there is a correct answer. The code is not clear on this issue.Poll Status to Date.
Those who have answered correctly :smile: --------- 33%
Those who have answered incorrectly :roll:-------- 60%
Those who are wayyyyy off------------------ 6%
Poll Status to Date.
Those who have answered correctly :smile: --------- 33%
Those who have answered incorrectly :roll:-------- 60%
Those who are wayyyyy off------------------ 6%
Be loyal to truth and a reference, not an opinion.....I turn my back on my opinions all the time
The above results are base on your opinion, not necessarily the opinion of all.
It all depends on how to read 250.122(A) & (F), which without a ruling from the NFPA cannot be decided by a handful of people here on the site.
(have you read 250.122(G) - which is a good example of how EGC can be sized accordingly with the ungrounded conductor. And....feeder tap conductor sizing in ratio can be much smaller in size relative to the overcurrent device size)
2005 NEC Handbook Commentary
Where wire-type equipment grounding conductors are installed in multiple raceways or cables used to enclose conductors in parallel, a full-sized equipment grounding conductor selected from Table 250.122 based on the size of the overcurrent device protecting the paralleled circuit is required in each raceway or cable.
2008 NEC Handbook Commentary
Where wire-type equipment grounding conductors are installed in multiple raceways or cables used to enclose conductors in parallel, a full-sized equipment grounding conductor selected from Table 250.122 on the basis of the size of the overcurrent device protecting the paralleled circuit is required in each raceway or cable.
NECPLUS.org
Staff Note for 250.122(F)
Where conductors are run in parallel raceways or cables as permitted by 310.4, each parallel equipment grounding conductor shall be sized per Table 250.122 based on the size of the overcurrent device protecting the conductors. In other words, the equipment grounding conductor in each raceway or cable must be full-sized, even though the ungrounded (phase) conductors are reduced in size.
Short of a Formal Interpretation or a statement from a code making panel published in the ROP or ROC, I don't see how you can say there is a correct answer. The code is not clear on this issue.
As I said in the other thread, if you are summing the total of all of the ungrounded conductors of one phase to say that the EGC in a single raceway is not larger than the circuit conductors, they why don't you use the same process and sum all of the EGCs to say that the EGC is in fact larger than the circuit conductors?
Obviously a single man.![]()
I would no be willing to make that bet as none of the cases address the issue here...where the EGC in a raceway is bigger than the phase conductors in that same raceway. If you are using 500 kcmil, you have to get above 4000 amps for the OCPD before the EGC is larger than 500 kcmil. It is my opinion that it is poor design to parallel when you need to have more than ten sets of conductors.See commentary in the 2005, 2008, and NECPLUS.org........:roll: Although commentary is not formal interpretations, I would be willing to bet that the code making panel would agree with the commentary in the handbooks and the staff note in necplus.org.
Why doesn't it? The only cable that can feed power into a fault in that raceway are the 1/0 phase conductors. Why can't a 1/0 EGC carry the fault current that is supplied by the 1/0 ungrounded conductor....
In a case where you are paralleling a large number of conductors (like paralleled 1/0 for a 5000a circuit) it certainly doesn't make sense that you could only use a 1/0 EGC.