The pool propane heater is on the same circuit it draws like 1.5 amps does this change your answer ?
Sent from my SM-G935V using Tapatalk
Also what wire Guage do I need for 120 feet of branch circuit wiring from breaker to pump in underground conduit ?
Sent from my SM-G935V using Tapatalk
It's 115v
Sent from my SM-G935V using Tapatalk
210.23 Permissible Loads, Multiple-Outlet Branch Circuits.
In no case shall the load exceed the branch-circuit
ampere rating. A branch circuit supplying two or more outlets
or receptacles shall supply only the loads specified
according to its size as specified in 210.23(A) through (D)
and as summarized in 210.24 and Table 210.24.
(A) 15- and 20-Ampere Branch Circuits. A 15- or
20-ampere branch circuit shall be permitted to supply
lighting units or other utilization equipment, or a combination
of both, and shall comply with 210.23(A)(1) and (A)(2).
(B) 30-Ampere Branch Circuits. A 30-ampere branch circuit
shall be permitted to supply fixed lighting units with
heavy-duty lampholders in other than a dwelling unit(s) or
utilization equipment in any occupancy. A rating of any one
cord-and-plug-connected utilization equipment shall not
exceed 80 percent of the branch-circuit ampere rating.
You still cannot have the heater on a 30 amp circuit
It's a propane heater. It probably uses the 120 for control circuits and a blower motor.
Yes, I know-- not sure what your point is..
How are the pump and propane heater NOT utilization equipment as per 210.23(B)? :?
So you are saying that a pump cannot be on a 30 amp breaker? If so look at 430.52---Motors are a different animal. Still not sure of what you are asking. I think the pump and heater are utilization equipment but pumps have an article unto themselves. The heater does not get permission in 210.23(B) as far as I can tell.
You do realize that Hayward pumps are notoriously troublesome with Hayward pumps.... A dp 20 amp gfci should work