Hello. What breaker & wire size?? I’m installing a 6000 watt heater @ 240 volts. So 6000/240=25 amps x 125% continuous load = 31.25 amps. Can I use a 35 amp two pole breaker & 10 awg? Can I use 10/2 romex or does it need to be THHN in pvc? Thanks
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Hello. What breaker & wire size?? I’m installing a 6000 watt heater @ 240 volts. So 6000/240=25 amps x 125% continuous load = 31.25 amps. Can I use a 35 amp two pole breaker & 10 awg? Can I use 10/2 romex or does it need to be THHN in pvc? Thanks
You cannot use number 10 anything.

Whether you use Romex or PVC is a design choice.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
is that using the 60 deg column?
There is a special rule for number 10 conductors that says you can't have more than a 30 amp over current protection device. I don't recall exactly where this is but it's like a note in the ampacity chart. There's like an asterisk next to the value in the chart and if you look down at the bottom there's another asterisk and it says you can't actually use the value that's in the 75° table for that size wire.
 

acin

Senior Member
Location
pacific grove california
Occupation
general building contractor est.1984 . C 10 elec. lic.as of 8 / 7/ 2020
There is a special rule for number 10 conductors that says you can't have more than a 30 amp over current protection device. I don't recall exactly where this is but it's like a note in the ampacity chart. There's like an asterisk next to the value in the chart and if you look down at the bottom there's another asterisk and it says you can't actually use the value that's in the 75° table for that size wire.
got it 240 4 d . unless 240 4 G
 