Hello. What breaker & wire size?? I’m installing a 6000 watt heater @ 240 volts. So 6000/240=25 amps x 125% continuous load = 31.25 amps. Can I use a 35 amp two pole breaker & 10 awg? Can I use 10/2 romex or does it need to be THHN in pvc? Thanks
You cannot use number 10 anything.Hello. What breaker & wire size?? I’m installing a 6000 watt heater @ 240 volts. So 6000/240=25 amps x 125% continuous load = 31.25 amps. Can I use a 35 amp two pole breaker & 10 awg? Can I use 10/2 romex or does it need to be THHN in pvc? Thanks
is that using the 60 deg column?You'll need #8 conductors.
There is a special rule for number 10 conductors that says you can't have more than a 30 amp over current protection device. I don't recall exactly where this is but it's like a note in the ampacity chart. There's like an asterisk next to the value in the chart and if you look down at the bottom there's another asterisk and it says you can't actually use the value that's in the 75° table for that size wire.is that using the 60 deg column?
got it 240 4 d . unless 240 4 GThere is a special rule for number 10 conductors that says you can't have more than a 30 amp over current protection device. I don't recall exactly where this is but it's like a note in the ampacity chart. There's like an asterisk next to the value in the chart and if you look down at the bottom there's another asterisk and it says you can't actually use the value that's in the 75° table for that size wire.
No it's because of 240.4(D) as acin mentioned.is that using the 60 deg column?