Sure there is. The pump is designed in when city pressure can't meet flow requirements for the structure. Most small commercial installs don't have fire pumps. Most large warehouse "boxes" do.Originally posted by davedottcom:
Is there such a thing as a sprinkler system without a pump?
That makes sense.Originally posted by bdarnell:
The pump is designed in when city pressure can't meet flow requirements for the structure.
Goerge, I don't have my code book in front of me but what does 240.4 (B) say to allow one to use any ampacity other than the 60 degree column allows?Originally posted by georgestolz:
60? column of 310.16 as tweaked by 240.4(B).
60? per 334.80.
Tom, you still use the 60 degree column, and you will see #6 NM is rated at 55amps, but you can use a 60 amp breaker since they don't make a 55 amp breaker. If it complies with 240.4(B)1,2&3 it is fine.Originally posted by m73214:
Goerge, I don't have my code book in front of me but what does 240.4 (B) say to allow one to use any ampacity other than the 60 degree column allows?Originally posted by georgestolz:
60? column of 310.16 as tweaked by 240.4(B).
60? per 334.80.
let me add this other standard breaker / fuse size is 601 amperes also240.6 Standard Ampere Ratings
(A) Fuses and Fixed-Trip Circuit Breakers The standard ampere ratings for fuses and inverse time circuit breakers shall be considered 15, 20, 25, 30, 35, 40, 45, 50, 60 , 70, 80, 90, 100, 110, 125, 150, 175, 200, 225, 250, 300, 350, 400, 450, 500, 600, 700, 800, 1000, 1200, 1600, 2000, 2500, 3000, 4000, 5000, and 6000 amperes.
As long as the Minimum Circuit Ampacity is 55 or less , you are correct.Originally posted by kg18:
The circuit is for a electric furnace with a 60 amp breaker. I believe I have won the bet. He wanted to run 4/3 but I said no way 6/3 is what we are pulling.