Alain Dappen
Member
what size conductor do i need to feed a 100 amp residential panel if my
source is 700 feet away?
source is 700 feet away?
iwire said:I bet at least a 4/0 copper assuming 100 amps of load and 240 volt.
What you really need is a couple of transformers, boost it to about 550 send it the 700' and then reduce it back to 120/240.
Along with reducing the wire sized needed you can also leave the neutral out and create a new one at the far end.
ptonsparky said:Don't know what leaving the neutral out would do.
Plus the homeowner gets to pay for two transformers, the inefficiency of both, the additional fusing and maintenance.
ptonsparky said:Using the 25kva load continuous for simplicity:
wasasparky said:I don't think a 104A continuous load is typical for a residence...
iwire said:When figuring voltage drop I would not consider continuous or not.
But I agree the 100 amp size is not the real load, it is all we have to go on yet.
6% impedance does not represent transformer lossses.ptonsparky said:Acme transformer says their dry type units are 6% impedance. Two units would be 12%. Your customer pays for this. Using the 25kva load continuous for simplicity:
KW*cost*hours*days= yearly cost
25*.10 (use local cost)*24*365= $21,900
Now add 12% because of transformer losses on the load side of the meter. I read that the typical life span is 30 years for an electrical installation. 30 years*$2628=$78840 just for the two transformers.
Alain Dappen said:what size conductor do i need to feed a 100 amp residential panel if my
source is 700 feet away?
Alain Dappen said:Thank you gentelman. We calculated 4/0 as well. Unfortunatly the costumer
(Gov't) requires 2% VD max, and our 2" conduit is already in the ground.
Pulling 3-4/0 in a two inch is max and a bear. We wonder if compacted cable
or some sort of deisel cable would be allowed.
Cost is no object to the Government. They are spending Other People's Money (OPM).Alain Dappen said:Thank you gentelman. We calculated 4/0 as well. Unfortunatly the costumer (Gov't) requires 2% VD max, and our 2" conduit is already in the ground.
Pulling 3-4/0 in a two inch is max and a bear. We wonder if compacted cable
or some sort of deisel cable would be allowed.
Alain Dappen said:Thank you gentelman. We calculated 4/0 as well. Unfortunatly the costumer
(Gov't) requires 2% VD max, and our 2" conduit is already in the ground.
Pulling 3-4/0 in a two inch is max and a bear. We wonder if compacted cable
or some sort of deisel cable would be allowed.