What size EMT

Status
Not open for further replies.

Nicksid

New User
Location
Newport, RI
What is the size EMT I will need for a 200A service from the meter to the service cap and meter? Also, is an outside disconnect mandatory by code now?


Sent from my iPad using Tapatalk
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
What size conductors are you using and how many-- ie- single phase or 3 phase etc? Also insulation type would be helpful
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
What is the size EMT I will need for a 200A service from the meter to the service cap and meter?

not enough information to give you an answer. conduit size is determined by conductor size and you did not tell us what size conductors you are using. I am not real sure you can even use EMT.

Also, is an outside disconnect mandatory by code now?

The NEC would not require one. However, there may be local requirements that do, or the POCO may require one.

Sent from my iPad using Tapatalk

1 characters
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree.

Of course if one wishes to nit pick, there is that UL thing Mark Ode brought up about a PVC male adaptor into a threaded hub.
True and that was brought up at one install we did and I stated that there were thousands of these installs all over NC and we have never had a problem. I told him we would use caulk around it after the install and he was agreeable.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree.

Of course if one wishes to nit pick, there is that UL thing Mark Ode brought up about a PVC male adaptor into a threaded hub.

You had to bring up my biggest pet peeve in 30 years of this business. :rant:
 