ohmhead
- ORLANDO FLA
Well i agree with Bob the pump is going to burn on the pad before it stops !
Heres a fire pump controller we had on one job http://i611.photobucket.com/albums/tt195/stringking/428.jpg
The feed from the generator was 500 mcm one run.
The feed from the poco transformer was 500 mcm .
The fire pump was a 200 hp 3 phase 480 v .
The 6 wire to the motor was 3/0 .
The brk in the genset was a 400 amp .
And no over loads used .
This was a ul listed fire pump controller and transfer switch in the fire pump room most power companys now ask to install a disconnect at transformer but we never do it its just a direct connection to the transfer switch .
But keep this in mind if you running this in conduit its underground or outside of the building in rigid pipe its a un protected feeder from that transformer .