Re: What size OCD?
Just today, copied the nameplate data from an Air Compressor.
Several decals on the unit noted 7 HP.
The Name plate data did not list HP. It did list voltage as 230V 1 PH 17.3 Amps. plus other data.
I do not have the 2003 UL White book at home to check against the 2002 UL White book.
Under (AALZ), which is at front of the numbered pages, and under "Sizing and Ratings" it notes that "Marked ratings of utilization equipment include ampere, wattage or volt-ampers ratings. Motor-operated utilization equipment may also be marked with horsepower rating. The actual marked ratings( other than horsepower rating ) and other markings or instructions, if any, are to be used to select branch circuit conductors, branch circuit overcurrent protection, control devices and disconnecting means."
So, don't install per the HP size, but per the amps or the watt or VA ratings.
T430.148 for a 230V, 17.3A would be consided as 3 HP +/-.
How deceitful these product promoters can be!
Several years ago, a similar installation for an Air Compressor. With-out looking-up the incident, I believe it had the same nameplate data as this unit today. The installer had used Number 10 AWG ( Cu ) on a 35 to 40 foot Branch Circuit. The owner called me back about a year later to tell me that the manufacturer, after burning-up two motors, told him to read the instructions, which I do not remember being on site at time of inspection. The owner had the instructions saying that Number 8 AWG ( copper ) must be used if branch circuit greater than 25 feet. The installer was contacted and I did not hear anything more.
gwz2
[ November 14, 2003, 06:36 PM: Message edited by: gwz2 ]