This thread has shined some light on this subject for me and I appreciate everyone's input. I wonder why my firm is so dead set on specifying only compression fittings and never set screw?
Sometimes old habits and beliefs die hard.
Roger
Agree enthusiastically and completely.It has always been, and still is, my opinion, that a set screw EMT coupling or connector is a better grounding connection than the grounding connection made by a compression coupling or connector. I have found many more loose or broken compression type couplings and connectors than I have set screw ones.
I hope you will spread the word.This thread has shined some light on this subject for me and I appreciate everyone's input. I wonder why my firm is so dead set on specifying only compression fittings and never set screw?
If you are saying that using the conduit as the EGC is hack work then I think you are wrong.Or you could just always make sure to run a separate EGC and not use conduit as a ground path - which I think is kinda hack, to be honest.
I'm inclined to agree with that too. I have seen such an attitude displayed by some of the "green to everything" guys I have worked with.It seems to me that he was trying to say that not taking any care about the raceway continuity just because you have pulled a wire EGC is hack work, and I am inclined to agree with that.
All those EGC's take up space in the raceway that could have maybe been used for an additional few circuits, unnecessarily uses more copper, and if you are going to pull more then one EGC if one needs spliced or connected to they all need to be brought into the same splicing device and bonded to the box and/or device. Pulling one sized for the largest overcurrent device makes the most sense to me, but I am also one of those that is most likely to use the raceway for the EGC in most instances.This is as per 2250.122(C). My question is, what do you do at the loads, splice the EGC and extend the ground to each load? I guess I am not used to this because we typically specify one EGC per circuit regardless.