pathfinders
- Cebu Philippines
- Consultant
I am a non qualified consultant operating in the Philippines.
A very large american owned international company is my client. I am a foreign consultant interpretting requirements and ensuring thigns are done propperly.
They have a site requirement of 150 KVA. Almost everything is specified out to the model number, however their documentation on required SPD is looking at WYE 3 phase system, without specifiying voltages.
So, we are intending to supply their equipment with 3 individual sets of single phase at 50 KVA each, ehere they all come from one 3 phase 3 pole main breaker supplied fomr a banked 3 phase delta set of transfomers. So thats 11 KV WYE into 3 individual 50kva singel phase transformers wired up in WYE-DELTA with absolutely no neutral on the low voltage side. Thats 3 conductors from the trasnformer to the main breaker, each 230V between each other.
This main breaker will have a 3 pole branch dedicated for a 3 pole surge protector.
Now, the question that no electrical engineer is able to make me feel comfortable about...
what should the rated voltage on an SPD be for this setup?
Each conductor would be about 110V to ground. so therefore, my brian tells me that i need a 3 pole 3 phase , but it needs to be reated to somethign close to 120 volts.
Am I correct?
If so, i cant seem to find such a device that has the specs i feel comfortable with. They seem sto suggest such a thing is onnly for a 110 votls system, which this is not, its a 230V delta. So what dose one look for?
Im not happy wtih the local explanations, everything just sets on fire here because no one realy knows their sciences or questions their knowledge.
Am I correct?