What to do after hurricane Helene

Roger9

Member
Location
Tampa
Occupation
Electrican
I’m unsure about a problem we’re facing over here in Florida. We’re getting calls to houses that were flooded due to hurricane Helene. receptacle's and some switches were submerged in salt water. Nobody can really get an answer from the county or inspectors on what needs to be done.

We know that any device or metal box that was submerged needs to be replaced but what do you guys think about the wire? If it’s cloth we’re replacing but we’re unsure about romex.
 
Ya but if you dry it out is it really comprised? Not like it’s been under ground for years
Maybe technically you have to but practically is what I am wondering
Flood water is generally contaminated, I would replace the romex. Until someone provides documentation that romex that has been submerged is safe for the long term, I'd replace it.

A study should be conducted to test water damaged romex as this has been and will continue to be a problem.
 
I hope not, it would be a waste of materials and labor. The romex would have already been secured and supported by the earth. 🙂
How many houses have been wired by qualified persons who were careful in securing and handling the romex?

Pinched wire + water/contamination = fire
 
Since it was salt water, I'd replace, fresh water, probably leave as is. Replace esp if covered by insurance.

Run megger test if unsure. There was a hydro generator station I was familiar with that flooded one year, fresh water. Put the whole thing in a tent with warm dry air for a couple of weeks (or longer in one generator case) till passed megger test. Returned to service, ran fine. Dont recall if it was 13.0 or a 25kV generators. Salt water likely would never pass megger tests.
 
Anyone know what the difference between wet and dry insulation is? Like what exactly happens to THHN if it gets wet?
Insulation itself? None really. PVC is very tolerant of saltwater. IIRC THHN is PVC.
The sulphides and ammonias in seawater are the most corrosive things to any copper. One of the reasons copper pipe isn't used for marine applications.
 
Insulation itself? None really. PVC is very tolerant of saltwater. IIRC THHN is PVC.
The sulphides and ammonias in seawater are the most corrosive things to any copper. One of the reasons copper pipe isn't used for marine applications.
I would be concerned about salt infusion. When salt dries it isn't conductive but when it gets wet it is.
 