• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

What to do after hurricane Helene

Merry Christmas

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I would be concerned about salt infusion. When salt dries it isn't conductive but when it gets wet it is.
Agreed.. but conductivity aside when the saltwater gets into the wire, it's very corrosive to the copper wires.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
How many houses have been wired by qualified persons who were careful in securing and handling the romex?

Pinched wire + water/contamination = fire
If they have removed wall covering because it too was submerged then you should be able to visually see said pinched wire if it exists?

Outside of paper fillers in the cable wicking up moisture I really don't see much issue with getting NM cable wet. Mold issues maybe.

As others have mentioned, I have also seen many cases of misused NM cable and wetness mostly only makes a mess of the paper fillers but the conductors are always fine.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I would be concerned about salt infusion. When salt dries it isn't conductive but when it gets wet it is.
If you choose not to replace, remember salt is also potentially corrosive. If you do not have the wire to spare to cut back, do your best to make sure the ends of the wires are clean and smooth surfaced.
 
Top