I did this service call in a tanning salon. There were 7 tanning booths with no power. There was a sub-panel that just had 7 breakers for these booths. The main panel was right next to it and the 100 amp breaker that fed the sub-panel was tripped, although it didn't look tripped but felt tripped when pushing it towards the on position (even though it appeared to be in the on position already).
I opened the panel cover of the sub-panel (3 phase) and the line colors on the buss lugs were black, red, and white! So I thought some dummy must have marked one of the legs the wrong color!
I tested voltage on the legs and from A-grnd. was 240, B-grnd. was 240, and C-grnd. was 0, and A-B was 244, A-C was 240, B-C was 240.
So they landed the neutral on C leg.
So you only have 2 hots, neutral , ground to this panel.
I noticed in the main panel inside the door it says 3 phase 600 amp 240 volt.
I've just never come across this type of service before. I don't think I've ever even heard of this.
What's also got me confused is one of the booths still wouldn't work even though the rest of them came back on after I reset the breaker.
But it did have power to it. I think it was just something wrong with it and it needs serviced.
But some of these 2 pole breakers that serve these booths are on B-C or A-C and some of the others are on A-B. So I'm very confused at how this is working and why some of them are getting 2 hot legs of 240 volts per leg with no neutral and others are getting just one hot leg at 240 volts and a neutral.
I didn't get to dive deeper into this as I had to pick up my daughter from school, but I would've liked to look into it with more time to snoop around, especially since I've never seen anything like this before.
I'd like to hear any and all opinions that I can.
Thanks.
I opened the panel cover of the sub-panel (3 phase) and the line colors on the buss lugs were black, red, and white! So I thought some dummy must have marked one of the legs the wrong color!
I tested voltage on the legs and from A-grnd. was 240, B-grnd. was 240, and C-grnd. was 0, and A-B was 244, A-C was 240, B-C was 240.
So they landed the neutral on C leg.
So you only have 2 hots, neutral , ground to this panel.
I noticed in the main panel inside the door it says 3 phase 600 amp 240 volt.
I've just never come across this type of service before. I don't think I've ever even heard of this.
What's also got me confused is one of the booths still wouldn't work even though the rest of them came back on after I reset the breaker.
But it did have power to it. I think it was just something wrong with it and it needs serviced.
But some of these 2 pole breakers that serve these booths are on B-C or A-C and some of the others are on A-B. So I'm very confused at how this is working and why some of them are getting 2 hot legs of 240 volts per leg with no neutral and others are getting just one hot leg at 240 volts and a neutral.
I didn't get to dive deeper into this as I had to pick up my daughter from school, but I would've liked to look into it with more time to snoop around, especially since I've never seen anything like this before.
I'd like to hear any and all opinions that I can.