The conductors connected to the line side (grid side) terminals of the former main breaker are service conductors, but the conductors connected to the load side terminals are feeder conductors. Since you said the ESS panel has the new "main breaker" aka service disconnect.Wondering how this violates 230.7 though. Its only the service conductors in the conduit to the ESS
Now if the two enclosures are touching with just a conduit nipple (a fitting) connecting them, then 230.7 is not violated. But if you have a short nipple, that's a 230.7 violation.
Cheers, Wayne