Yes, that is .406 for every 10 feet and 40 feet would be just about 1-5/8".My code book says 100 degree F is a 4.06 inch change per 100 feet
Yes, that is .406 for every 10 feet and 40 feet would be just about 1-5/8".My code book says 100 degree F is a 4.06 inch change per 100 feet
Yes, that is .406 for every 10 feet and 40 feet would be just about 1-5/8".
pvc is 3.6" per 100ft @ 100F diffYes, that is .406 for every 10 feet and 40 feet would be just about 1-5/8".
Whole year. You need to know the change in length between the shortest the pipe will be and the longest the pipe will be.
If it was installed at less than full expansion it will tend to buckle to take up the additional length.
If it was installed at less than full contraction it can pull ends or even joints lose when it shrinks.
You really think those conductors get any wetter than normal during a flood ( gets pretty wet down there during a rain) and you are not making taps or splices down there. The conductors would need to be rated for wet location anyway.
Cost is normally what it always boils down to.
When an inspector inspects a job like this they don't do a stress test on the anchors and straps.
It's a visual inspection and this job probably met code requirements. These are listed straps and if the required number were used it would have appeared to be OK. Not only that but the job probably looked fine when the inspector saw it.
pvc is 3.6" per 100ft @ 100F diff
or 0.036" per ft
40ft is just about 1.44" @ 100F diff
~1.44 to ~1.625, sounds about right.
that expansion has to go somewhere, and if the end points of a round tube do not flex the tube will bow, and a bow from ~1.5" linear expansion will be pretty good.
Gee, the news on this keeps getting better and better :weeping: This installation was done in February of this year.
Thanks again for all of the details - this is extremely helpful.
Is it a simple matter to add the expansion fitting? It seems that it would not be because doesn't everything have to be disconnected and re-pulled through the conduit? Where does the expansion fitting need to get added? Anywhere along that 30-40 foot run?
Yes, you'll have to pull the wire out to put in expansion joints. It looks to me like those PVC pipes are toast, anyway. I'll bet you'd never get them looking straight again.
If it's a south facing wall, PVC will always look like limp noodles after the first summer.
But no expansion joint was used as you guys are emphasizing is required. Why would the inspection not pick up on that if it is a code requirement?