Measured with a high impedance meter, probably about the same as if grounded. With a low impedance meter, hard to say.If the GEC is removed from the utility transformer, what will the voltage be from ungrounded conductor to the earth?
If there is no defined reference, than the voltage is undefined. Because of capacitive coupling the measured voltage will be affected by the meter itself. I would expect to see something in the range of 277V to 960V on a normal 480Y/277V system.
Phantom voltage is a real voltage, but it is capacitive in nature, so the amount of energy that can be transferred across that capacitor is PROBABLY small, but not zero. I wouldn't make it a habit of touching live parts just because there is no direct conductive path between me and ground.Are these phantom voltage or measurable voltage?
In this case, since the earth does not have a path back to the source, then a person should not get shocked.
I agree that I should not make it a habit of getting between live parts and the ground given in my example. However, if I happen to touch, will one get shocked??Phantom voltage is a real voltage, but it is capacitive in nature, so the amount of energy that can be transferred across that capacitor is PROBABLY small, but not zero. I wouldn't make it a habit of touching live parts just because there is no direct conductive path between me and ground.
Absolutely, with a high-impedance meter that will not make the voltage collapse.Are these phantom voltage or measurable voltage?
That depends on many variables, but I wouldn't bet yours or anyone else's life on it.In this case, since the earth does not have a path back to the source, then a person should not get shocked.
How high is the voltage, how long is the transmission, how well are you earthed, etc?I agree that I should not make it a habit of getting between live parts and the ground given in my example. However, if I happen to touch, will one get shocked??
Lots of variables come into play to determine if you can get shocked through capacitive coupling. I have done a demonstration where I hold the non-contact voltage tester in one hand and touch a live 120 volt wire with the other hand, while standing on a pallet. I don't feel anything but the tester beeps. I did it with 277 volts and could feel a tingle when I touched it. I suspect that if the humidity were higher I would feel it more, but I won't chance it anymore over 120.I agree that I should not make it a habit of getting between live parts and the ground given in my example. However, if I happen to touch, will one get shocked??
Your body becomes the bonding jumper, not totally different than a high impedance ground. Don't be doing this when another fault occurs.In this case, since the earth does not have a path back to the source, then a person should not get shocked.
I don't see it in the '20. Is it new?“Voltage to Ground” for ungrounded circuits is defined in Article 100.
I have been able to pull in a wiggy measuring from a conductor of an ungrounded system to earth a few times....more than enough current for a serious shock.I agree that I should not make it a habit of getting between live parts and the ground given in my example. However, if I happen to touch, will one get shocked??
Looks like you missed it. From the 2020 NEC:I don't see it in the '20. Is it new?
The definition has been around since I’ve been in the business. It’s primary use is for clearancesI don't see it in the '20. Is it new?
Voltage to Ground.
For grounded circuits, the voltage between the given conductor and that point or conductor of the circuit that is grounded; for ungrounded circuits, the greatest voltage between the given conductor and any other conductor of the circuit. (CMP-1)
I didn't do it at the pole, but I just did it on the GEC at this office I am at. With the main breaker off, there is 2.7 amps... Meaning that the current is actually flowing INTO the service neutral from the earth. I disconnected the GEC and measured the voltage between it and the neutral as 0.15 V. So the entire circuit must be 0.05 ohms.Anyone ever put an Amprobe on the GEC for a pole transformer?