160813-1024 EDT
iwire:
For some information on current levels that nerves can detect see https://en.wikipedia.org/wiki/Electric_shock .
Now to phantom voltage. It seems this is generally defined as a voltage that is read by a high impedance meter that disappears when a low impedance is placed across the meter.
Basically the phantom voltage source has a high internal impedance.
Some internet discussion on phantom voltage:
http://support.fluke.com/find-sales/Download/Asset/2105317_A_w.pdf
http://www.allaboutcircuits.com/textbook/direct-current/chpt-3/ohms-law-again/ this has good information.
Capacitance in wiring or cables is what normally determines the leakage current that leads to phantom voltage readings.
Look at Romex construction. There are three wires, two are current carrying, and the third is the EGC. The physical topology has the EGC centered between the two current carrying wires. Thus, the capacitance between each current wire and EGC is the same and is proportional to cable length The phantom voltage on an isolated EGC is not dependent upon current flow in the current carrying wires, but on the AC voltage difference between the current wires. Since the two capacitance values are equal the EGC should be at a potential halfway between the two current wires.
The equivalent circuit is a voltage source equal to 1/2 the voltage between the two current wires and an internal impedance from the sum of the two capacitors. In reality there are other factors that modify this equivalent circuit some. The original post had somewhat unequal voltages. Thus, there are external factors that modify the circuit. For example the meter internal impedance.
.
iwire:
For some information on current levels that nerves can detect see https://en.wikipedia.org/wiki/Electric_shock .
Now to phantom voltage. It seems this is generally defined as a voltage that is read by a high impedance meter that disappears when a low impedance is placed across the meter.
Basically the phantom voltage source has a high internal impedance.
Some internet discussion on phantom voltage:
http://support.fluke.com/find-sales/Download/Asset/2105317_A_w.pdf
http://www.allaboutcircuits.com/textbook/direct-current/chpt-3/ohms-law-again/ this has good information.
Capacitance in wiring or cables is what normally determines the leakage current that leads to phantom voltage readings.
Look at Romex construction. There are three wires, two are current carrying, and the third is the EGC. The physical topology has the EGC centered between the two current carrying wires. Thus, the capacitance between each current wire and EGC is the same and is proportional to cable length The phantom voltage on an isolated EGC is not dependent upon current flow in the current carrying wires, but on the AC voltage difference between the current wires. Since the two capacitance values are equal the EGC should be at a potential halfway between the two current wires.
The equivalent circuit is a voltage source equal to 1/2 the voltage between the two current wires and an internal impedance from the sum of the two capacitors. In reality there are other factors that modify this equivalent circuit some. The original post had somewhat unequal voltages. Thus, there are external factors that modify the circuit. For example the meter internal impedance.
.