- Location
- Massachusetts
Jim W in Tampa said:Possably the grounding conductor is carrying part of a bad neutral from the house feeding it.
That may be a stretch but it is certainly possible and that is a good point.
Jim W in Tampa said:Possably the grounding conductor is carrying part of a bad neutral from the house feeding it.
quogueelectric said:If there is current on it there will be voltage drop. Oh no here we go again. Real life VS desk theory.
dicklaxt said:This has to be an induced voltage from something maybe even the test meter its self.IMO,,,,, hence Phantom Voltage,at play possibly?
dick
Stray or ghost voltages occur from capacitive coupling between energized circuits and non energized, non connected adjacent wiring. Because of this coupling effect and the multimeter?s high impedance, it?s not always possible to determine if the circuit under test is energized or de-energized, and this creates confusion for the person performing the test.
Midwest is the most highly visible panel pushed by the supply houses by me lots of displays and heavy marketing so I would assume they sell in other parts of New York also. Just my gut feeling by information provided. They make a pretty nice panel.iwire said:So I have to ask, Why would you assume it's 'Midwest pool panel' and why would you assume enough current on the EGC to cause 5 volts of drop? :-?
True - which why I was asking why/what is this person testing for.iwire said:I did not see anything the tells us what the load on the neutral is.
I just do not believe in ghosts - if there is a measured voltage there - it is there, be it capacitive or induction, it is there - usable as if it would sustain any load - different story - still not a ghost.... Might be enough to give you a really neat ground loop hum, or effect sensitive electronics. But not enough to show up on your Wiggy...dicklaxt said:This has to be an induced voltage from something maybe even the test meter its self.IMO,,,,, hence Phantom Voltage,at play possibly?
Voltage potential reference to ground should be "0" when measuring from the grounded conductor to the grounding conductor
It too is a return path for testing purposes here, and one often of a smaller conductor, and with often many more connections. (Some that are often paid less attention to.) Sure you will get zero right there in the main panel, but then put a few dozen connections, some through conduit lock-nuts, and various bars, and yes you will get some losses, take that another hundred feet, and get some more, put some/any current on the neutral and you are going to have differences. Same can be said for the neutral it self - testing both together at a distance is that - testing them both.LarryFine said:Why would the EGC have any voltage drop?
I aggree, but first I would do it with the supply on, and no load - then supply off.dbuckley said:I would repeat the voltage measurement with the supply off, and see if the voltage changes. That will determine if its volt drop is due to neutral current or ground current.
I agree....Remember, high levels of N-G voltage invariably arise from grounding/bonding problems.
Which is why I continue to use my Knopp K-60 (now CAT-III rated).e57 said:But not enough to show up on your Wiggy...
Oh, I didn't realize you were intentionally loading the EGC.It too is a return path for testing purposes here, and one often of a smaller conductor, and with often many more connections. (Some that are often paid less attention to.) Sure you will get zero right there in the main panel, but then put a few dozen connections, some through conduit lock-nuts, and various bars, and yes you will get some losses, take that another hundred feet, and get some more, put some/any current on the neutral and you are going to have differences. Same can be said for the neutral it self - testing both together at a distance is that - testing them both.LarryFine said:Why would the EGC have any voltage drop? :-?
Cow tongue?quogueelectric said:How long are you gonna keep us hanging with our tongues out here???
Failing to get your point.... Mine was if you are measuring potential differences N-G at long distances from the main bonding jumper that there will be just that. Difference's in potential.... Neither conductor is identical - and in this case carrying an unknown current. And 5 volts... I do not see it as consequential for some applications... Nor do we know the full testing circumstances.LarryFine said:Quote:
Quote:
Originally Posted by LarryFine
Why would the EGC have any voltage drop?
It too is a return path for testing purposes here, and one often of a smaller conductor, and with often many more connections. (Some that are often paid less attention to.) Sure you will get zero right there in the main panel, but then put a few dozen connections, some through conduit lock-nuts, and various bars, and yes you will get some losses, take that another hundred feet, and get some more, put some/any current on the neutral and you are going to have differences. Same can be said for the neutral it self - testing both together at a distance is that - testing them both.
Oh, I didn't realize you were intentionally loading the EGC.
Was this all on one phase???? Is the ground conductor resistive? Is the neutral?118 ft from its source. The conductors are 4 AWG, with an actual load of around 16-19 amps.
That, under normal conditions, there should be no current on the EGC.e57 said:Failing to get your point....
dicklaxt said:I asked my friend this who happens to be the smartest man I have ever known,,,,here's what he contributes.