Actually some have the correct hot stick and cut the overhead at the pole. Or just pull the cutout on the line side of the pole transformer.
That could be. But our poco would never let that happen.
Actually some have the correct hot stick and cut the overhead at the pole. Or just pull the cutout on the line side of the pole transformer.
If there is any fire and/or the Main breaker does not open, call the fire department, call the fire department....did I mention to call the fire department.
It becomes their responsibility. While doing so, try to evacuate the house/building without putting yourself or anyone at too much risk.
Both are dangerous, if I had to make a choice I would rather cut the drop from the safety of a bucket truck.
Meters are not designed to open a load and if you have a serous fault on the load side of the meter it may have several hundred amps passing through it. When you pull it you could cause an arc that would result in a flash over.
Depending on the severity I would call the FD, let them deal with it.
They have great phone numbers for fast action from the POCO and can deal with any progression of the problem.
iwire said:On the other hand if you try to pull a meter or cut a drop that is under fault conditions you may be successful or it could blow up in your face. My safety rates higher to me then someones property.
The power company might not like it but there is not much they can do about it. The Fire Department has a lot of legal authority at the scene of a fire or other emergency to take the actions they deem necessary to mitigate the emergency.That could be. But our poco would never let that happen.
thats what I was thinking as well. However, I would also consider cutting the seal, taking off the meter ring, and hitting the meter out of its socket with a 2x4 standing to the side of it. [I have a 12' 2x4 in my side yard, which is why I thought of that]
It would still depend on the situation, I'd probably just call 911.
~Matt
But of course there is never a chance a firefighter will get hurt fighting the fire.....In this area it is not uncommon to have a power company response time of well over an hour, even when dispatch makes it very clear that it is a real emergency. I don't think any of our local FDs have the training or equipment to cut the drop or pull the cutout, but if I had the proper tool, I would not really hesitate to cut the service drop at the pole or pull a cutout so the fire can be safely fought. I don't see making the cut or pulling the cutout as being any where near as dangerous as going into the building to make the primary search or fight the fire. (assuming proper training and equipment)Even if you have a Hot Stick and its been properly maintained and you are a master electrician and you are a firefighter, you don't pull that cut out or sever that service drop!!!!!!!!
If this was a Life Safety Issue e.g., trapped occupant in a vehicle fine go ahead.
(personally and professionally I find that the wrong thing to do).
But, it the POCO's job to do so. Its just property. There is a slight small chance that someone (firefighter) could get hurt disconnecting the power and there are no lives at risk you don't do it!!!!
Disclaimer: I am not one of those wussy guys that say oooh too much fire don't go in!!! (Don, you must know what I mean.) I just think there is a balanced approach in this individual situation.
Makes you wonder why we don't just install an exterior disconnecting means.
Even just a non-fused switch for this exact purpose.
Makes you wonder why we don't just install an exterior disconnecting means.
Even just a non-fused switch for this exact purpose.
busman said:The following happened to a good friend of mine. He was called for dimming lights and strange smell. When he gets there, the panel is starting to melt-down. He throws the main breaker, but the short continues. What do you do?