What's a box-out for floor boxes?

Status
Not open for further replies.
Little Bill

I am reading a spec; we are supposed to install floor data & power outlets. To run conduits via ceiling of floor below. To provide dimensions of "box-outs" for steel floor boxes before concrete pour. I am lost on the "box-out" part. Could it be a crude way of saying dimensions of boxes?

Thanks

Steve

I don't understand your question?
 
You literally put a wooden box (say 2'X2') or some other material (we have used layers of Styrofoam) on the deck before the concrete is poured. The box-out is removed and electrical box is installed after the concrete is poured and the box-out is patched with the box in it. This allows for the box to be set to the proper height and exact dimensions after the deck is poured. We once did a job where they wanted the floor boxes centered on the intersection of 4 tiles, we installed the box-outs prior to the pour and then the tile guy layed out his seams on the concrete and we set the boxes from there.
 
We did a concrete floor that had 32 floor boxes. We couldn't box it out so the boxes had to go in first. Of course, they wanted the rectangular boxes not the round ones. What a nightmare but we got it. They did not want patched in the floor that had color added to it
 
But were these box outs on grade? The OP said the conduits were to run in the ceiling below, so I assume this is an upper level.

Seems like they would use poke throughs and not floor boxes?
 
But were these box outs on grade? The OP said the conduits were to run in the ceiling below, so I assume this is an upper level.

Seems like they would use poke throughs and not floor boxes?

All depends on what the designer wants. Poke throughs are limited in size when compared to some large floor boxes.
 
All depends on what the designer wants. Poke throughs are limited in size when compared to some large floor boxes.

i guess I always thought that a big box in the middle of an elevated floor slab would weaken the slab. But I guess the structural designer deals with it. Maybe they run rebar around the cutouts?
 
i guess I always thought that a big box in the middle of an elevated floor slab would weaken the slab. But I guess the structural designer deals with it. Maybe they run rebar around the cutouts?

Yes typically there is extra rebar if the penetration is very large. We often have penetrations for conduit runs that can 15-20 square feet, the lather usually reinforces the area with extra rebar under the direction of the structural engineer.
 