I'm working on a renovation project which required us to turn two old rooms into one new electrical room, i.e. we removed the wall between the spaces to make one room for all the new electrical gear.
We have one switchboard that is 2000A and it is longer than 6'0", plus several smaller panelboards.
We only have one entrance/exit to the electrical room. (continuous and unobstructed path from the equipment to the door).
Problem is, the architect found a structural issue with removing the wall between the two rooms. He added the dividing wall back between the spaces and put a passageway through the wall. The passageway is just a 3'0" cased opening through the wall.
I let him know that the passageway idea wouldn't work because we no longer have an unobstructed path away from the equipment to the exit door. And of course, his response is how wide do we need to make the passageway in order to consider it an unobstructed path.
Now I'm stumped. Best I can tell is that we will have to use two egress doors now.
Or can we make that passage wide enough that the path of egress is considered unobstructed? Also, is the cased opening even consdered a door?
What do you guys think?
We have one switchboard that is 2000A and it is longer than 6'0", plus several smaller panelboards.
We only have one entrance/exit to the electrical room. (continuous and unobstructed path from the equipment to the door).
Problem is, the architect found a structural issue with removing the wall between the two rooms. He added the dividing wall back between the spaces and put a passageway through the wall. The passageway is just a 3'0" cased opening through the wall.
I let him know that the passageway idea wouldn't work because we no longer have an unobstructed path away from the equipment to the exit door. And of course, his response is how wide do we need to make the passageway in order to consider it an unobstructed path.
Now I'm stumped. Best I can tell is that we will have to use two egress doors now.
Or can we make that passage wide enough that the path of egress is considered unobstructed? Also, is the cased opening even consdered a door?
What do you guys think?