In a discussion regarding residential branch circuits, my electrician tells me that a TAP includes lighting outlets and receptacles. His position is that every set of pigtails off a branch circuit to provide for a receptacle is a TAP, and therefore the Table at 210.24 limits a 15 or 20a residential circuit to a total of 14 outlets of all kinds.
We agree that we can't find a definition of TAP in the NEC.
I believe that there is no limit to the number of receptacles on a residential branch circuit, provided it serves only general use and lighting under 220.3(B)(10) (1), (2) & (3). which says those receptacles fall under the 3VA / sq.ft. general load calculation. Instead, I think the limit is the area that the circuit may serve, based on the 3VA rule.
I do agree with him that other branch circuits, such as the small appliance circuits, do limit the number of receptacles by requiring a calculation of 180VA per yoke.
So - What's the definition of a TAP?
and - is there a limit on the number of general use receptacles?
Let the opinions fly.
We agree that we can't find a definition of TAP in the NEC.
I believe that there is no limit to the number of receptacles on a residential branch circuit, provided it serves only general use and lighting under 220.3(B)(10) (1), (2) & (3). which says those receptacles fall under the 3VA / sq.ft. general load calculation. Instead, I think the limit is the area that the circuit may serve, based on the 3VA rule.
I do agree with him that other branch circuits, such as the small appliance circuits, do limit the number of receptacles by requiring a calculation of 180VA per yoke.
So - What's the definition of a TAP?
and - is there a limit on the number of general use receptacles?
Let the opinions fly.