Strathead
Senior Member
- Location
- Ocala, Florida, USA
- Occupation
- Electrician/Estimator/Project Manager/Superintendent
That would be ideal. Unfortunately, they don't always know what every receptacle is for. And, it would be time consuming to request that of lets say 600 receptacles. I was just looking for a way to do it myself based off of the NEC's definition of convenience receptacle. But, there doesn't seem to be one.
You are making it way too difficult. I understand, that it isn't as simple as Cowboy states, but I think he missed the fact that you are asking from an Engineer/designer perspective, not an Electrician, but what I told you has NOTHING to do with requesting what 600 receptacles are for. If you have a large facility you used 600 receptacles that is probably about 30,000 square feet. Say it is an office. Ask are any offices designated for special use? I see 2 break rooms, what appliances do you anticipate? What kind of machinery do you currently use in your mail room? Do you expect to use any large copy machines outside the mail room and if so where? Look at the Architectural. Rooms will or should already be designated. So, if you see a special room ask about it. Cold Storage... Oh yeah, that is for 3 freezers, because our salesmen bring iced drug samples to our customers for example. Worry only about those items! make sure there is enough power for them, count the rest and use 180va and viola you are done. It is not that complicated, don't make it so.