Re: What's in the box?
If this 100 amp circuit was feeding a welder or a compressor, it would be a "branch circuit, individual" because it would be the last overcurrent device supplying one utilization equipment.
Since it is feeding a panel in a detached garage, it is a "feeder". The circuit breakers in that panel will feed the branch circuits in the garage. Even if you only install one branch circuit initially, it is still a feeder because more branch circuits can be added to the panel, and the last overcurrent device still is in that panel.
Look in you 2002 NEC Handbook, page 25, exhibit 100.5 for a clear distinction between feeders and branch circuits. Also read the definitions for branch circuit and for feeder.
310.15(B)(6) specifically says it only applies to a feeder to a dwelling ("...feeder conductors that serve as the main power feeder to a dwelling unit...") A detached garage isn't a dwelling unless it specifically meets that definition (the definition at the front of the code book, Article 100). This would probably be a judgement call for the AHJ, but most of them that I know wouldn't let you use table 310.15(B)(6) for a feeder to a detached garage.
How did you come up with needing a 100A feeder and panel for the garage? Do the loads there require that size panel? If you are wanting to use #4,can you get by with using a circuit breaker rated at or below its adjusted amp rating?
Was this a bid job?
If you are doing it by the hour, I'd just feed it with #2, a 100/2 CB in the main panel, and use a 100A MCB panel in the garage, and get on with it. A MCB panel will probably be cheaper, and you can kill the whole panel locally if you need to work on it or if something serious happens in the garage.