Coppersmith
Senior Member
- Location
- Tampa, FL, USA
- Occupation
- Electrical Contractor
I'm estimating a job where I come out of the panel in a house, go through the attic, come out the side of the house, go underground for 20 feet, come up outside a detached garage, go through the wall and terminate at a subpanel. Customer has requested 100 amps. Please double check my thinking here.
Aluminum would be a lot cheaper than copper so I should avoid copper solutions.
I can't use SER cable because it's not allowed underground either direct buried or in conduit.
I can't use SEU cable because it's not allowed in the attic due to it not being fire rated.
Seems like the least expensive way would be 3 x AL #1 XHHW and #6 CU ground in conduit from end to end. I'll use EMT in the attic and on the outside walls. I'll use IMC for the underground which means it only has to be buried 6". I'll run the IMC out of the ground and up the wall about 18" for physical protection from lawn mowers then change over to EMT. I can't use PVC in the attic due to it's 122 degree temperature limitation.
Do you see any code violations in my proposed solution? Anybody got a less expensive way to do this?
Here's another way that I don't think will fly with the HO, but I'm curious if it's code complaint: Run a messenger cable between the buildings and use SER cable the entire way. The SER will be attached to the messenger with UV resistant zip ties. I believe SER can be exposed to weather and sunlight. Compliant?
Aluminum would be a lot cheaper than copper so I should avoid copper solutions.
I can't use SER cable because it's not allowed underground either direct buried or in conduit.
I can't use SEU cable because it's not allowed in the attic due to it not being fire rated.
Seems like the least expensive way would be 3 x AL #1 XHHW and #6 CU ground in conduit from end to end. I'll use EMT in the attic and on the outside walls. I'll use IMC for the underground which means it only has to be buried 6". I'll run the IMC out of the ground and up the wall about 18" for physical protection from lawn mowers then change over to EMT. I can't use PVC in the attic due to it's 122 degree temperature limitation.
Do you see any code violations in my proposed solution? Anybody got a less expensive way to do this?
Here's another way that I don't think will fly with the HO, but I'm curious if it's code complaint: Run a messenger cable between the buildings and use SER cable the entire way. The SER will be attached to the messenger with UV resistant zip ties. I believe SER can be exposed to weather and sunlight. Compliant?