If the cord set has a permanent inline GFCI that can not be removed without cutting it, why couldn't we have something like 10/2 +16/1 or 12/2+16/1?
Cord sets are not intended for permanent installation and having a full size EGC essentially capable of indefinitely serving as "neutral" through a ground fault into case seems silly. Since you can buy 16 AWG extension cords, 16AWG copper or perhaps 16 CuAl clad would seem adequate for mechanical strength purpose while serving enough conductivity to allow GFCI to work.
The reduced weight without compromising on performance is a big plus.
Cord sets are not intended for permanent installation and having a full size EGC essentially capable of indefinitely serving as "neutral" through a ground fault into case seems silly. Since you can buy 16 AWG extension cords, 16AWG copper or perhaps 16 CuAl clad would seem adequate for mechanical strength purpose while serving enough conductivity to allow GFCI to work.