Was the person who made the termination qualified? That is did he get all of the semi-conductor insulation off of the dielectric insulation when he installed the stress cone?
It was done so long ago that nobody even knows who built it.Was the person who made the termination qualified? That is did he get all of the semi-conductor insulation off of the dielectric insulation when he installed the stress cone?
If it's not prohibitive to de-energize for a few hours, I'd have some new tape and cleaner handy, shut it down, remove discolored portions of tape, and assess... then clean and re-tape no matter the assessment, and re-energize.It was done so long ago that nobody even knows who built it.
I'm wondering if we ought to try and re-terminate it or replace the whole cable.
Check anti condensation heater inside panel enclosure. If defective, replace it.
The corona onset voltage decreases with increase in air humidity. An operating anti condensation heater would avoid it and so the damage shown in the photo of the OP.
Wouldnt stress cones do the same?
Check anti condensation heater inside panel enclosure. If defective, replace it.
Does it imply no working heater in your panel?I can see how an anti-condensation heater could cause over-heating, say due to a thermostat with welded contacts.
Neither have I.I have never seen any pictures of corona damage that looked like what is shown in this thread.
Here's how the other loop conductors are terminated at the opposite end of the gear.
View attachment 14842