Whats wrong with this?

Status
Not open for further replies.

ronaldrc

Senior Member
Location
Tennessee
Thought I would try a new thread.

Can you find anything wrong with this diagram?

:)

[ September 01, 2003, 11:40 PM: Message edited by: ronaldrc ]
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Whats wrong with this?

Ronald I'm probably way off base, but are we using an ungrounded delta here? (accidental starting or shunting around the stop switch)

Roger
 

templdl

Senior Member
Location
Wisconsin
Re: Whats wrong with this?

There is no protection for the control circuit such as a fuse. Being that the control is taken from L-L there should be (2) fuses. Also, How does the TC get energized if the TC contact is NO and is closed by the TC?
 

ronaldrc

Senior Member
Location
Tennessee
Re: Whats wrong with this?

Russ is close, look at the start button when you push it, it energizes M which is the starter coil which starts the motor.


The second post was right thats right the TC can't start timing out because it never sees power.


I don't know what kind of delay this is pneumatic or solid state. Either way the NO TC contact is in series with TC coil.

The TC coil can't be energized this way because of NO TC.The motor would continue to run with the resistors in the rotor circuit it would never pick up to full speed.


The only other answer is it is a simplified diagram and not showing all the controls but I don't think so because it doesn't mention that and it doesn't show any wire conn. take offs for other controls.


Ronald :)

[ September 01, 2003, 08:33 PM: Message edited by: ronaldrc ]
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Whats wrong with this?

templdl
There is no requirement in Art 430 for fuses in a control circtuit tapped from the motor branch circuit, as shown here. See section 430.72(A). However if fuses are installed then the motor control circuit follows the rules in Art 725, see last sentance in 430.72(A)
 

ronaldrc

Senior Member
Location
Tennessee
Re: Whats wrong with this?

Thanks for confirming the circuit is drawn wrong.

Truth is if where a pneumatic starter with two pneumatic NO contacts that NO contact wouldn't even be needed.

I no everyone makes mistakes but the bucs we pay out for these books you would think they could look over them a little better.

Ronald :)
 

Ed MacLaren

Senior Member
Re: Whats wrong with this?

I wonder why the contact which is (erroneously) marked "TC" is shown in a seperate enclosure, and what operates it?
The way it is wired, it energises the TC coil.

And the two contacts above the TC coil should be identified "TC".


Here are a couple of different Wound Rotor Motor controls that I think will work OK.

One is a 3-step starter, and the other is a 3-speed controller.

WRR1.gif


WRR2.gif


Ed
 

ronaldrc

Senior Member
Location
Tennessee
Re: Whats wrong with this?

Ed thanks for the diagrams look good to me.

Magnetics made things easy.Large solid state are functionly better but I don't trust them. I like mechandical contacts for isolation.
Of course thats why we have disconnects I guess.

Like I said I'm not certain about that delay circuit on that drawing if there are more controls not shown? If so it usually says so.

Remember the old oil type manual like a transfere switch.Those where the days.

Ronald :)
 

ronaldrc

Senior Member
Location
Tennessee
Re: Whats wrong with this?

David that would work could be? Looks like it would say. This diagram was scanned directly from the 2002 NEC handbook and no changes where made.

Thanks:Ronald :)
 

ronaldrc

Senior Member
Location
Tennessee
Re: Whats wrong with this?

David thats a good call and I believe it is right. I just reread all the information on those pages it didn't mention a centrifugal
switch.

But I am going to assume it is a centrifugal switch untill someone tells me different.

It does show it in a separate enclosure.

Thanks:Ronald :)
 

templdl

Senior Member
Location
Wisconsin
Re: Whats wrong with this?

Tom Baker,
My referrence is NFPA 79 (my copy is 1997), 8.9 Control circuit conductors. Your statement is correct when the circuit meets the requirements of the exceptios as I understand it.
8.9 General, and 8.9.2 Conductor Protection. Both 8.9.2.1 and 8.9.2.2 both state that they shall be protected in accordance to their ampacities or not more than a 20a rating for conductors #14 and smaller.
However, if the control circuit falls within the exceptions that are incuded in this section then and OCPD is in fact not required as you have stated.
 