Re: Whats wrong with this?
Tom Baker,
My referrence is NFPA 79 (my copy is 1997), 8.9 Control circuit conductors. Your statement is correct when the circuit meets the requirements of the exceptios as I understand it.
8.9 General, and 8.9.2 Conductor Protection. Both 8.9.2.1 and 8.9.2.2 both state that they shall be protected in accordance to their ampacities or not more than a 20a rating for conductors #14 and smaller.
However, if the control circuit falls within the exceptions that are incuded in this section then and OCPD is in fact not required as you have stated.